Devices > Remote Devices > DNP3 Emerson EIE > UIS Command Component Parameters

UIS Command Component Parameters

The following tables list and describe the parameters specific to the UIS command component types for this remote device:

For more general information about UIS command component parameters, see UIS Command Components. The DG_F_DEV (Get data group from device) and DG_T_DEV (Send data group to device) command component types are configured in the template file. The other command component types are considered ‘special’ and are defined in the EIE editor code. See Special UIS Command Component Types for more information.

CLRHSTXA

Clear All History Tx Info clears all historical data group caches. CLRHSTXA has no command parameters.

Note: If you clear all caches using a UIS command, the cache values in each transaction of historical data groups are not reset; past transactions continue to display actual values. This is done for performance reasons so that each DDS transaction does not have to be updated. The driver ignores these cached values after the command has been issued.

CYUPDTPT

Update CygNet Point updates the record for a CygNet point. CYUPDTPT has the following command parameters:

Parameter Required Description

FOnErr

No

Fail cmd on update error indicates to abort the UIS command if any update errors are encountered. The errors that might come up include: if the point specified in the Fac, Serv, Site, or UDC parameters does not exist, or if the point exists in a different UIS and any messaging errors or communication failure to that service comes up.

Fac

Yes

Facility for pt identifies the facility of the point to update.

Serv

No

Service for pt identifies the SERVICE of the point to update.

Site

No

Site for pt identifies the SITE of the point to update.

UDC

Yes

UDC for pt identifies the UDC of the point to update.

UType

No

Update type indicates the type of update. Value options are 0 - 3, where 0=Completion, 1=Success, 2=Failure, 3=Creation.

UsrMsk

No

User bit mask specifies the user bit mask of the point to update.

UsrVal

No

User bit value to match specifies the user bit value to match when updating the point record.

Value

No

Value indicates the point value to update.

CYWAITPT

Wait for CygNet Point signals the UIS to wait to perform a command until the value of the specified CygNet point changes to a specified value.

CYWAITPT must be the first command component added to a UIS command. You cannot add other instances of CYWAITPT to a UIS command.

CYWAITPT has the following command parameters:

Parameter Required Description

Dur

Yes

Duration is the amount of time (in HH:MM:SS or HH:MM or HH) for the UIS command to wait for the point value to change before timing out.

FOnErr

No

Fail on point error indicates to abort the UIS command if any error conditions are encountered. The point errors that might come up include: if the point specified in the Fac, Serv, Site, or UDC parameters does not exist, or if the point exists in a different UIS and any messaging errors or communication failure to that service comes up.

Fac

Yes

Facility for pt identifies the facility of the point on which to wait for the point value to change before performing the UIS command.

Int

Yes

Interval indicates the frequency (in HH:MM:SS or HH:MM or HH) with which the UIS will check the point’s value to see if it has changed.

Serv

No

Service for pt identifies the SERVICE of the point on which to wait for the point value to change before performing the UIS command.

Site

No

Site for pt identifies the SITE of the point on which to wait for the point value to change before performing the UIS command.

UDC

Yes

UDC for pt identifies the UDC of the point on which to wait for the point value to change before performing the UIS command.

UsrMsk

No

User bit mask specifies the user bit mask on which to wait for the status bit change before issuing the UIS command.

Note: The user status bit parameters (UsrMsk and UsrVal) only apply to the extended status field of the point record, so they will not match anything in the base status.

UsrVal

No

User bit value to match specifies the user bit value to match before issuing the UIS command.

Value

No

Value to match specifies the value on which to wait for the point to change to before issuing the UIS command.

Note: You can set parameters for both the point user status AND point value. So you can match either one by itself, or you can specify that both must match your parameter values.

DG_F_DEV

Get data group from device retrieves a data group from a field device. The Parent XML Element is uccRecvParms. The following parameters are available for each specified data group type.

Data-Group Type Parameter Required Description

Data Groups containing dgCat="File"

FileName

Yes (see Note in Description)

Name of file to read.

Value options are strings.

Note: The parameter is required only when the data group is missing a value for fileName in the device template.

Event

Class1

No

Get class 1 events

Value options are Boolean.

Class2

No

Get class 2 events

Value options are Boolean.

Class3

No

Get class 3 events

Value options are Boolean.

Count

No

Max events

Value options are integers.

ptType

No

Point type

Value options are strings.

Variation

No

Point type variation

Value options are integers.

HistAlarm

Cnt

No

Max Records to Read specifies the maximum possible number of records to read in a single transaction.

Value options are integers.

EDate

No

End date defines the ending date and time.

Value options are strings.

GetLatest

No

Get Latest? defines whether or not to retrieve history from the latest successfully read history record (the cache).

Value options are Boolean.

SDate

No

Start date defines the starting date and time.

Value options are strings.

Seq

No

Sequence # defines the first sequence number in the requested range.

Value options are integers.

HistEvent

Cnt

No

Max Records to Read specifies the maximum possible number of records to read in a single transaction.

Value options are integers.

EDate

No

End date defines the ending date and time.

Value options are strings.

GetLatest

No

Get Latest? defines whether or not to retrieve history from the latest successfully read history record (the cache).

Value options are Boolean.

SDate

No

Start date defines the starting date and time.

Seq

No

Sequence # defines the first sequence number in the requested range.

Value options are integers.

HistGenD

HistGenH

HistGenM

HistGenW

HistStaD

HistStaH

HistStaM

HistStaW

HistUser

Cnt

No

Max Records to Read specifies the maximum possible number of records to read in a single transaction.

Value options are integers.

EDate

No

End date defines the ending date and time.

Value options are strings.

GetLatest

No

Get Latest? defines whether or not to retrieve history from the latest successfully read history record (the cache).

Value options are Boolean.

SDate

No

Start Date defines the starting date and time.

Seq

No

Sequence # defines the first sequence number in the requested range.

Value options are integers.

SinglePt

DataType

No

Data Type defines the type of data stored at the specified point type.

Value options are strings.

Desc

No

Description

Value options are strings.

ElementId

Yes

PointType.Index specifies the point type and index number values used to retrieve data from a single element.

Value options are strings.

FacUdc

No

Facility.UDC for point processing provides a means to specify a UDC to which to map the specified data point; it requires a corresponding point in the Point Service (PNT).

Value options are strings that specify a Facility.UDC combination.

Variation

No

Point type variation

Value options are char values.

DG_T_DEV

Send data group to device sends a data group to a field device. The parent XML Element is uccSendParms. The following parameters are available for each specified data group type.

Data-Group Type Parameter Required Description

IntInd

IIN1.7

No

Device Restart

Value options are Boolean.

SinglePt

Clear

No

BO: Clear

Value options are Boolean.

Count

No

BO: Count

DataType

Yes

Data Type defines the type of data stored at the specified point type.

Value options are strings.

Desc

No

Description

Value options are strings.

ElementId

Yes

PointType.Index specifies the point type and index number values used to retrieve data from a single element.

Value options are strings.

FacUdc

No

Facility.UDC for point processing provides a means to specify a UDC to which to map the specified data point; it requires a corresponding point in the Point Service (PNT).

Value options are strings that specify a Facility.UDC combination.

Len

Yes (String point type only)

Len specifies the number of bytes in a data-group element or register. Only used for String point type.

Value must be a positive whole number.

PulseLatch

No

BO: Pulse/Latch/No-op

Value options are strings.

TimeOff

No

BO: Time off (ms)

Value options are integers.

TimeOn

No

BO: Time on (ms)

Value options are integers.

TripClose

No

BO: Trip/Close

Value options are strings.

Value

Yes

Value defines a value to be sent to the specified item.

Value options are floating-point numbers.

Variation

No

Point type variation

Value options are char values.